Adding to what toolndye_dave said about the bus caps — that's the #1 hidden cause on older MR-J4 units in my experience. Here's how I diagnose it systematically:
1. Monitor parameter Pr.52 (DC bus voltage display) on the MR-J4 during a full-speed forming stroke. If it dips more than 30% from idle, your caps are suspect. Healthy caps on a 200V system should hold above 260VDC even under peak load.
2. Check the cap ESR if you have an ESR meter. Mitsubishi doesn't publish a spec, but as a rule of thumb, if ESR is more than 2x the original value (usually printed on the cap label), replace the whole bank. Don't cherry-pick individual caps — if one is gone, the others are close behind.
3. The sneaky one: ambient temperature. MR-J4 caps are rated for 85°C typically. If your cabinet cooling fan died 6 months ago and nobody noticed, you've been cooking those caps at 50-60°C instead of 35°C. That halves their life per the 10°C rule.
4. Timing matters too. If AL.10 only happens on the first stroke after a long idle (like Monday morning), the caps might be fine but need a soft-start charge cycle. Some older MR-J4 firmware versions have a known issue where the pre-charge relay timing is too short after extended power-off. Mitsubishi released a firmware update for this around 2019 — check if you're on the latest.
One last thing — if you're getting AL.10 intermittently and can't reproduce it, check your incoming power during peak plant load times. We had one that only triggered between 7:00-7:15 AM when the whole shop was starting up simultaneously. A 3% voltage sag at the utility level was enough to push the bus below threshold during a heavy forming stroke.