One more thing on the intermittent SV0447/0448 — if you've checked the cable and shielding and it's still happening, look at the encoder connector on the motor side. On Fanuc αiS motors the connector has a locking tab that wears out over time. The connector looks seated but under vibration it micro-disconnects for a few milliseconds. Enough to trigger 0448.
We had one that drove us nuts for 3 months. Cable tested fine, shielding was good, routing was textbook. Finally put a zip tie as a secondary retention on the motor-side connector and it never came back. Three cent fix after weeks of troubleshooting.
The summer/temperature correlation pressroom_tom mentioned is real too. Thermal expansion of the connector housing changes the contact pressure. If your alarms cluster in the afternoon when the shop is hottest, that's your clue.