The speed feedback filter point mike_blanking raised is huge and I want to expand on it. Parameter 90.41 is one of those "set it and forget it" values that can bite you months later.
Here's the scenario I've seen twice now: someone tunes the drive for a high-speed blanking job (40+ SPM), sets the speed filter higher to smooth out the feedback noise at high velocity. Works great. Then the die changes to a slow forming job at 8 SPM with a 200ms dwell. Now the filter is masking the low-speed signal and you get phantom 7121s.
My rule: if you change 90.41 for a specific job, write the original value on tape on the cabinet door. Better yet, save it in the parameter set (group 61 on ACS880 lets you store 4 complete parameter sets). We use Set 1 for blanking, Set 2 for forming, Set 3 for deep draw. Operator selects via DI — no manual parameter changes needed.
Also — if you're getting 7121 only on the first 5-10 strokes after a cold start, check the motor thermistor reading (parameter 09.11). Cold motor winding resistance is higher, which throws off the current model. The ACS880 motor model adapts but it takes a few cycles. Extending 31.26 (stall time) by 2-3 seconds for the warm-up period is a reasonable workaround.