Adding a PM angle to this thread. We track F30015 on our S120 fleet (4 presses) and saw it cluster around shift starts in winter — points to thermal/condensation issues rather than pure firmware. Two things that cut our occurrence rate ~60% over 18 months:
1. Cabinet heater + dewpoint sensor on the drive bay. Anything below 8°C cabinet temp on cold mornings was correlated with first-cycle F30015 events. $180 in hardware, paid back inside a quarter on avoided callouts.
2. Quarterly clamp-on logging at the LCL filter terminals. We caught a degraded contactor on one press that was producing dirty switching transients only under load — easy 5kA spike fix that explained months of intermittent faults.
For documentation: we keep a one-page "F30015 first-response card" laminated in each cabinet — p0864 / p0840 check, DC bus voltage threshold, then escalate. Took the average MTTR on this fault from 35 min to 8 min for our shift techs. Happy to share the template if anyone wants it.